johnieG
|
|
« Reply #11 on: June 04, 2020, 08:49:10 pm » |
|
your 3-in-1 is the correct size range for your application, I mean does the compressor not run for very long so the machine doesnt get down to temperature?
short cycling the compressor isn't very helpful because you're stopping it in the middle of a run cycle then slamming it on again & short-cycling it to your compressors going to see some loading from the back-pressure in the system when it's trying to restart that can cause the overload in the 3-in1 to turn off the motor until it cools down to attempt to restart again
so, from a normal start, how long does it run until the compressor shuts off?
does it run long enough to get down to the thermostat setting?
once it's down to temp & the machine loaded with beverages what you'd be shooting for in an ideal run cycle is about a 60/40 duty cycle 60 % of the time it's off, 40 % of the time it's on ( to maintain the temperature setting)
hard to say what your system pressure is doing, you cant put any gauges onto the system unless you install some clamp-on service valves, I prefer to braze on permenent valves myself, by again this involves recovering the freon & opening the system to cut the lines & braze the valves in place. add on valaves are handy for diagnoising a system, they can be prone to leaking if installed incorrectly ( say on a dirty/corroded or bent section of line, or selecting the wrong size tubing size adapter,) I polish the lines prior to installed the add on valves to make sure the copper is clean of paint & corrosion for the best seal.
but you can kinda get an idea of how the system charge is doing by observing the evaporators frosting zone & how far up the evaporator tubing rows it goes, with an room temperature of about 70-deg F (20-C) & the evaporator fan running, ( thermostat at max. cold) you should be able to see the first 2 or 3 sets of "Elbows" of the tubing frost up lightly at first, now another test is if you temporarily block the evaporator fan from rotating by gently jamming a rag into the fan blades so the cant turn ( before you turn the machine on obviously) you will now see the frost work its way row by row from the front to the rear of the evaporator coils up into the large copper sausage ( the accumulator we discussed earlier) which should get quite cold & even possibly frost over itself until you remove the jammed fan rag.
so with the evap' fan running you should see 1 or 2 rows frost, if only the tip of the capillary tubing frosts ( think of capillary tube as a piece of hollow copper spaghetti ) ( just where it enters the larger evaporator tube) before the compressor shuts off, or the system runs & runs but doesn't get down to temperature, then you may have an under charge system , which means the ris a slow leak somewhere that needs to be addressed.
or if it seems that the system doesn't run long enough, but the evap' coils seem to be trying to get cold, you may have a bad thermostat, or the wrong type for your machine, (if you've replaced it) , to test for a bad 'Stat ( power off) remove the wires from the rear of the control , temporarily short/jumper them together & insulated them from shorting to the metal chassis & start the compressor & see if it runs longer , it should run until you unplug the machine, don't leave it this way unattended with drinks inside, unregulated the machine can get down to as cold as 24-degrees F & freeze your bottles to bursting
|