Author Topic: Temperature Just Wont Get Low Enough  (Read 6479 times)
0 Members and 1 Guest are viewing this topic.
RMphy89
Newbie
*
Offline Offline

Posts: 6


« on: August 11, 2015, 02:59:10 am »

Hello everyone,

My Vendo 110's cooling system has been testing my patience lately. Granted the machine isn't perfect, but it was working pretty well just a few weeks ago. And those few weeks ago is when I installed a new thermostat. Before the thermostat went in, the machine was actually getting too cold, about 29 or so. I put the thermostat in and got it to run well (Cooling to 32 and cutting back in at about 42) Now when the machine gets to about 35 / 36 the temperature starts to go back up! And the compressor is still running. Any ideas what could cause this? I did rewire the light inside the door, which required me to remove the inner door panel, could the door seals not be seating correctly? A refrigerant issue? Thanks!
Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5396


This is fine...everythings going to be OK....


WWW
« Reply #1 on: August 11, 2015, 09:08:07 pm »

I assume you didnt use the "$1.99 special", as cheap t-stats tend to drift, just a thought.
Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
Slapshot42
Soda Jerks
*****
Offline Offline

Posts: 2629


Jared


« Reply #2 on: August 11, 2015, 11:33:23 pm »

Did you order a contact or noncontact t stat?  If you have a contact and the end of the probe isn't touching the cabinet directly that could be causing the problems.

Also there are "cut in" and "cut out"set screws on the t stat to adjust when the t stat turns on and off.  If the t stat is out of adjustment it could be shutting off before it gets cold enough ...

I'm NO expert I just recently bought a new one for a customer and the instruction provided explained it a bit!

« Last Edit: August 11, 2015, 11:35:05 pm by Slapshot42 » Logged
RMphy89
Newbie
*
Offline Offline

Posts: 6


« Reply #3 on: August 12, 2015, 12:01:48 am »

Thanks for the replies. I believe the thermostat is working correctly. The unit was cooling correctly with the new thermostat before. My problem right now is that the temperature gets to about 35 and then rises abruptly, all while the compressor is still running. So in essence the compressor never shuts off and the temperature just bottoms out at 35 and then rises again.

Also, I'd like to note that every time the unit has done this, I've unplugged the machine and plugged it in a few minutes later. After I plug it back in the compressor refuses to start until it cools off (You can hear the little klixon element clicking on and off inside) The weird thing is that The compressor is still running when I unplug the unit. I don't know why the klixon decides to trip after the cord has been pulled.
« Last Edit: August 12, 2015, 12:17:38 am by RMphy89 » Logged
cohammer
Soda Jerks
*****
Offline Offline

Posts: 961



« Reply #4 on: August 12, 2015, 01:21:37 am »

Sounds like you just need a better thermostat if the compressor cools that good . Or get the thermostat bulb in the correct position.
Logged

Ideal 35 RC
v 23 deluxe
v 39
c 96
c 55 e
C 51 g
C 72
C96
V 27
Westinghouse JR ice chest
Westinghouse standard ice chest
Westinghouse master ice chest
early model Stoner jr.
Stoner theaters
Thanks Jeff
MoonDawg
Soda Jerks
*****
Offline Offline

Posts: 6227



« Reply #5 on: August 12, 2015, 07:45:07 am »


 After I plug it back in the compressor refuses to start until it cools off (You can hear the little klixon element clicking on and off inside)


          Your system is telling you something.
          While the compressor is running it is building up pressure in the high side lines.
          When you unplug it, the high side pressure must be reduced to equal low side pressure before it will start again.
          I have found 5 minutes to be ample time.
Logged