« on: April 06, 2012, 09:06:00 pm » |
|
My ideal 35 slider had a hole in the suction tube, repaired hole ,pulled a vac,held a vac for 2 days ,then put 8 oz of r 12 back in. now its not cooling and about every 5 min the suction line will frost for a few minutes and then just go back to sweating here are a couple of pictures of line and pressure , any help wanted.
|
|
|
Logged
|
Ideal 35 RC v 23 deluxe v 39 c 96 c 55 e C 51 g C 72 C96 V 27 Westinghouse JR ice chest Westinghouse standard ice chest Westinghouse master ice chest early model Stoner jr. Stoner theaters Thanks Jeff
|
|
|
johnieG
|
|
« Reply #1 on: April 07, 2012, 12:01:30 am » |
|
be aware that just because a system holds a vacuum, it doesn't mean that there isn't still a leak, you never rely on suction to test a system for leaks, you must be able to maintain pressure,
Your symptoms are classic & indicate moisture in the system plugging the capillary tube ( thus the low suction line reading) with ice crystals, which melt, then the line frosts on the outside until the ice plugs the capillary again, then you loss freon flow & the system warms again & repeats the cycle. if the system was exposed to air/atmosphere, then you should have replaced the filter/dryer after you pressure check the system.
|
|
« Last Edit: April 07, 2012, 12:14:45 am by johnieG »
|
Logged
|
Spoon-feeding Newbies since 2001... Yeah..220,221 whatever it takes. Remember, all it needs is a shot of Freon! The Vendo V-83 is the '59 Edsel of the coke machine world. ;p Spray painting does NOT restore a compressor 11 is louder than 10... "Hope" is good, but it's not an action plan.
|
|
|
cohammer
|
|
« Reply #2 on: April 07, 2012, 07:17:26 am » |
|
sounds like a good possibility I think I will change the dryer and see if that does it. I am sure it had an open hole for a while.Do you recommend and certain model dryer? Thanks for the help it will give me a good start .And one other question could a 30 year old tank of freon be contaminated by rust or any thing on inside if tank?I always pull a vac and then turn every thing off and let it stay on vac for a while and see if it drops. How does every one else check for leaks?
|
|
« Last Edit: April 07, 2012, 07:42:57 am by cohammer »
|
Logged
|
Ideal 35 RC v 23 deluxe v 39 c 96 c 55 e C 51 g C 72 C96 V 27 Westinghouse JR ice chest Westinghouse standard ice chest Westinghouse master ice chest early model Stoner jr. Stoner theaters Thanks Jeff
|
|
|
Yarochrehc
|
|
« Reply #3 on: April 07, 2012, 08:34:40 pm » |
|
Refrigerant doesn't go bad, leaks are usually checked with nitrogen pressure, and you should always change the filter.
|
|
|
Logged
|
Bob
Restored Vendo H63B Coke in use in basement Original Vendo V/VF63/7 Pepsi in use
Restoring: Glascock Standard (2) Vendo 63 (2)Vendo 90 Vendo 126 waiting for paint VMC 56 Westinghouse WE-6
|
|
|
cohammer
|
|
« Reply #4 on: April 07, 2012, 08:59:34 pm » |
|
Did check for leaks with nitrogen . I changed the dryer maybe better luck this time.
|
|
|
Logged
|
Ideal 35 RC v 23 deluxe v 39 c 96 c 55 e C 51 g C 72 C96 V 27 Westinghouse JR ice chest Westinghouse standard ice chest Westinghouse master ice chest early model Stoner jr. Stoner theaters Thanks Jeff
|
|
|
johnieG
|
|
« Reply #5 on: April 08, 2012, 11:42:12 am » |
|
You didn't say if you were just watching the pressure in the system ( I assume you are) for any loss of charge, I use nitrogen & a touch of refrigerant with a sniffer to inspect my re-work, I also use UV dye injected into the system to highlight any future leaks...
|
|
|
Logged
|
Spoon-feeding Newbies since 2001... Yeah..220,221 whatever it takes. Remember, all it needs is a shot of Freon! The Vendo V-83 is the '59 Edsel of the coke machine world. ;p Spray painting does NOT restore a compressor 11 is louder than 10... "Hope" is good, but it's not an action plan.
|
|
|
cohammer
|
|
« Reply #6 on: April 09, 2012, 07:21:11 am » |
|
I did sniff all the joints as well as watching pressure but it still does not cool to suit me.I think I am throwing out the pancake and putting in a new compressor this may be the case a compressor from late 40 has sat idle too long with a hole on lines.
|
|
« Last Edit: April 09, 2012, 07:39:35 am by cohammer »
|