I have a Choice Vend CVC-224. Up until recently it ran great. Then I noticed the compressor began cutting out but the condenser fan continued to run, never did this before, in the past when the comp. cut off so did the cond. fan.
Now the problem has progressed to the point that the comp. only ran for about 15 seconds and stops. I topped off the R-12 as I needed to last year when I aguired the machine but no change. I bypassed the cold control no change and installed a 3-in-1 starter booster today and it would run a bit longer, maybe a minute then the comp. cuts out. One thing I noticed is if I unplug the evaporator fan plug the unit will continue to run and the evap. temp will get to 30 degrees and falling, as soon as I plug the evap. plug back in, within seconds the conpressor cuts off again. If you continue to let it run the comp. kicks back on but only for seconds.
With the evaporator plugged in, at about 85 degrees ambiant, the High Side pressure ran about 125 psi and the low side ran about 37 psi, are these in the range?
I'm at a loss, am I looking at a compressor here? any help would be appreciated. Thanks in advance.. Denny
Logged
globalcompressors
Soda Jerks
*****
Offline Offline

Posts: 839


Global Compressors (Eric)


WWW
« Reply #1 on: July 19, 2004, 10:02:31 pm »

Denny,

  37 psi on the low side is too high, 125 psi on the high side
is too low. Do you or did you notice the compressor getting
hot to the touch? Was the lower condenser coil dirty or have any kind of air flow blockage? What it sounds like, is the compressor has lost a valve. The pressure should be more in line with 8-12 psi, low side and 150 or so high. It's like you've
lost compression and the pressures are out. Kind of like a
350 V8 putting out only 100 hp bacause it's worn out or has bad valves. I'm curious, do you have a leak in the system or was it just not getting cold enough? Sometimes, if there is a problem, it may not always be freon related and adding freon can do more damage than good.


Eric