Author Topic: VT25 upper unit freeze up  (Read 5274 times)
0 Members and 1 Guest are viewing this topic.
Randy G
Newbie
*
Offline Offline

Posts: 3


« on: June 24, 2015, 05:17:50 pm »

Please let me thank Jim for kindly getting me set up to access this terrific knowledge base.  I have owned a Vendo H 63 A with a VT25 refrigeration unit for quite awhile.  I have done a partial restoration over time myself (paint, body filler, gaskets, decals).  The VT25 unit is original - but with an successful update several years ago by Alan Huffman.  The unit still cools (thermo setting 1-2), but the upper unit frosts up over approximately 10 days.  The compressor appears to run continuously.  The upper unit fan runs continuously as well - no problem.

I have to unplug the machine to defrost.  I have replaced the main door gasket and vending door gasket within the year.  I assume that ambient air intake is minimal to the bottle area.

I am obviously not refrigeration knowledgeable.  Any help you can provide me in troubleshooting is MOST welcome. No issues with previous work, just have a very old unit and need a solution.

I would like to gain some understanding of cooling issues and find a local solution to avoid shipping the unit.

Thank you very much for your time and kindness.
Randy Gray
Logged
MoonDawg
Soda Jerks
*****
Offline Offline

Posts: 6227



« Reply #1 on: June 24, 2015, 05:47:13 pm »

       Welcome Randy.
       Sorry to see that your successful update has turned unsuccessful.  darn
       Your system is now low on freon, possibly due to a very slow leak at a recent solder joint.
       Remove the unit again and take it to any refrigeration service center.
Logged

Glen
Randy G
Newbie
*
Offline Offline

Posts: 3


« Reply #2 on: June 25, 2015, 02:04:06 pm »

Thanks very much for your time, Moondawg.  I guess successful sometimes really means "successful for awhile".

I understand that the refrigerant used is "hot shot".  If I am having it repaired, evacuated and recharged, is that what I want to use, or do you suggest another refrigerant?

Thanks again for helping me out.
Randy
Logged
MoonDawg
Soda Jerks
*****
Offline Offline

Posts: 6227



« Reply #3 on: June 25, 2015, 03:23:34 pm »

         The unit originally used R-12, it's really cold stuff.
Logged

Glen