Author Topic: Evaporator coils freezing/frosting - unit not cooling  (Read 5200 times)
0 Members and 1 Guest are viewing this topic.
brasskey
25 Cent Member
****
Offline Offline

Posts: 308


« on: June 25, 2012, 07:46:34 pm »

So I checked the drinks this morning and they were nice and cold.  Evaporator fan was running and compressor/condenser fan was off at the time.  I just got home from work and the compressor and both fans were running.  But, the drinks were not cold.  I opened up the unit and the evaporator coils are completely frosted over.  Any ideas what the problem might be?





Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5396


This is fine...everythings going to be OK....


WWW
« Reply #1 on: June 25, 2012, 08:50:49 pm »

The Evap' coil fins are plugged with frost/ice due to an air leak letting in too much humid air, this flow of warm air forces the T-stat to keep the compressor running, then you get a film of frost over the fins & it ( bad pun warning) snowballs from there  tounge so shut off the T-stat, let it defrost & track down where the air leak is coming from.

Or it could be a stuck thermostat too.
« Last Edit: June 25, 2012, 09:22:46 pm by johnieG » Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
brasskey
25 Cent Member
****
Offline Offline

Posts: 308


« Reply #2 on: June 25, 2012, 09:11:02 pm »

The Evap' coil fins are plugged with frost/ice due to an air leak letting in too much humid air, this flow of warm air forces the T-stat to keep the compressor running, then you get a film of frost over the fins & it ( bad pun warning) snowballs from there  tounge so shut off the T-stat, let it defrost & track down where the air leak is coming from.

Or it could be a stuck thermostat too.

I'll check the door seals to see if too much hot air is getting in.  Then I'll replace the thermostat if that doesn't' fix it.  Thanks johnie.
« Last Edit: June 25, 2012, 09:22:31 pm by johnieG » Logged
globalcompressors
Soda Jerks
*****
Offline Offline

Posts: 839


Global Compressors (Eric)


WWW
« Reply #3 on: June 26, 2012, 07:33:56 am »

I like snow balls!   biggrin