When you call and talk to Janet let her know that you need both fan motors for your Cav 64
 and they can set you up. smile
Logged
cocacola
Newbie
*
Offline Offline

Posts: 23


« Reply #21 on: November 04, 2010, 05:04:14 pm »

Ok finally discovered more problems,

Now when we plug it in it causes a ground fault just to the outlet, it does not trip the breaker inside.

We isolated the following items,

The thermostat works fine
The evaporator and condensor fans work
There is a new service cord and all wires work
Coils on the compressor work
Started to test the switches

Now we also tried to hook the compressor motor to the outlet with jumper cables (sort of) and we got nothing

I really hope that it isnt the compressor motor but something still is not working.
One last question
What should be the ohm reading on the compressor?

Please if anyone can help, it has been a great experience so far
Logged
loman4ec
Soda Jerks
*****
Offline Offline

Posts: 4768



« Reply #22 on: November 04, 2010, 05:29:00 pm »

Where are you located? I may have a spare cooling system if it is dead. It is not the exact system but it will work.

Let someone else chime in to confirm this first but I would try a 3 in 1 starter before declaring the compressor dead.
Logged
cocacola
Newbie
*
Offline Offline

Posts: 23


« Reply #23 on: November 04, 2010, 05:40:07 pm »

Im in South East Wisconsin, so yeah...the whole thing did work for a bit in my possession so I really have no clue.
Logged
bubba
Soda Jerks
*****
Offline Offline

Posts: 3021



« Reply #24 on: November 04, 2010, 06:36:06 pm »

I think there was something posted awhile back about plugging into a GFI outlet.. Mine seem to work fine, but I believe there was a discussion about not using a gfi outlet..
Logged

Ken

V-63 -Bottles
2-Cavalier USS-64
VMC ST56B Royal Crown - being built
Vendo HA56C Coke
2-V63C DP
V63C Coke
U-Select-It 5cent candybar machine
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #25 on: November 04, 2010, 07:42:41 pm »

Most old soda machines have excessive leakage current to ground/earth due to deteriorated wiring insulation both in the wiring harnesses & the internal windings of the compressor motor itself, some machines chug-along just fine until a evaporator circulation motor or condenser cooling fan motor gets wet or damp & "CLICK"  , Your compressor seems to have developed a problem, so don't be surprised if your GFI protected outlet trips.

Every compressor has a different Ohms reading for the start vs the run winding, (as measured from the common terminal)  but generally speaking, the start winding is typically double the run windings reading, see the attached diagram for an example, hope it helps...
« Last Edit: November 04, 2010, 07:52:54 pm by johnieG » Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
loman4ec
Soda Jerks
*****
Offline Offline

Posts: 4768



« Reply #26 on: November 04, 2010, 07:56:58 pm »

That makes sense . So the first step troubleshooting is try an unprotected outlet. 
« Last Edit: November 04, 2010, 09:20:05 pm by johnieG » Logged
Creighton
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 4938


« Reply #27 on: November 04, 2010, 10:01:25 pm »

Good info there JohnieG. Thanks!!
Creighton
Logged
cocacola
Newbie
*
Offline Offline

Posts: 23


« Reply #28 on: November 10, 2010, 09:31:27 pm »

Ok so once again I the soda machine gods blessed me with a simple fix. When we rewired it, 2 hot wires accidently crossed so that's what caused the ground fault.

Lets see how long it takes for something else to happen.... hopefull

Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #29 on: November 11, 2010, 10:58:25 pm »

Good news "Sparky"   tounge
Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...