Author Topic: C-72 Icing up  (Read 7079 times)
0 Members and 1 Guest are viewing this topic.
kstt
5 Cent Member
**
Offline Offline

Posts: 91


« on: July 28, 2010, 12:05:06 pm »

I resurrected a Cav 72 about four years ago, including having the compressor replaced. It's been working fine, but recently, the front of the evap and the lines near it, are getting really iced up. Is this a problem? What is the most likely problem, and why does it seem to be recent problem?
Logged
MoonDawg
Soda Jerks
*****
Offline Offline

Posts: 6224



« Reply #1 on: July 28, 2010, 12:25:26 pm »

      Check to see if the fan behind the coils is spinning fast.
Logged

Glen
kstt
5 Cent Member
**
Offline Offline

Posts: 91


« Reply #2 on: August 02, 2010, 09:24:53 am »

The fan seems to be running fine. It was hard to see, because I couldn't see through the ice. I removed the tennis-ball-sized round plate in the center, and then could verify the fan is running well. By then, the ice was melting - even though the machine was still running. So, I let it melt before I closed it up. BUT - I also found that the lines from the compressor, UNDER the cold box, were also heavily iced. What's going on here?
Logged
MoonDawg
Soda Jerks
*****
Offline Offline

Posts: 6224



« Reply #3 on: August 02, 2010, 09:36:42 am »

       The thermostat may not be shutting the compressor off when desired temperature is reached. It's easy to replace.
Logged

Glen
kstt
5 Cent Member
**
Offline Offline

Posts: 91


« Reply #4 on: August 02, 2010, 10:48:49 am »

If the thermostat were the problem, wouldn't the product be freezing? Should I just try adjusting the thermostat to a warmer position?
Logged
collecture
Soda Jerks
*****
Offline Offline

Posts: 6959


Tom


« Reply #5 on: August 02, 2010, 01:26:03 pm »

If the thermostat were the problem, wouldn't the product be freezing? Should I just try adjusting the thermostat to a warmer position?
Most of my machines cool great with the t-stat set to 3
Logged

Cav 27, 33, CS-55E-2, 72
S-48 DP
Ideal CC 35, Barq's 55
1930s DP Counter Cooler
Vendo Coin Changers (ea. style - orig w/ stand)
Vendo Junior (rest.), 23 Deluxe, 39D, 44, 56RT, 80SS, 81A (orig), 81D, 6 C.V.
VMC 27, 27A, 81D DP, 110 DP
Westy WC-42-T, WC-44SK, WD-5(2), WB60
Victor C-14
Larry
Grady
Soda Jerks
*****
Offline Offline

Posts: 1979



« Reply #6 on: August 02, 2010, 02:18:14 pm »

Icing is usually lack of airflow (dirty coil, fan not working) or low charge of refrigerant.  Any oil leaks detected?
Logged

A lot of stuff.
kstt
5 Cent Member
**
Offline Offline

Posts: 91


« Reply #7 on: August 03, 2010, 05:19:56 am »

I don't have a tester. But, how long could it leak, and still stay cold?
Logged
houstonhusker
Newbie
*
Offline Offline

Posts: 14


« Reply #8 on: August 20, 2010, 12:42:56 pm »

I'm having the same issue with my USS-8-64.  Did you find out the source of the icing up?  I've tried adjusting the T-stat but no luck...
Logged
kstt
5 Cent Member
**
Offline Offline

Posts: 91


« Reply #9 on: August 31, 2010, 09:19:55 am »

Nope, not yet. I tried adjusting the "coarse" T-stat adjustment warmer. It's still 34 sometimes, in the box. That may be the trouble. I need to get it warmer, yet, I guess.
Logged