SMC Discussion Areas
November 27, 2024, 09:54:53 am *
Welcome, Guest. Please login or register.

Login with username, password and session length
News:
 
   Home   Help Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: Vendo 44 icing  (Read 6345 times)
0 Members and 1 Guest are viewing this topic.
Guest
« on: November 12, 2002, 11:10:02 pm »

Eric, thanks for your help on the capillary spefications.
I have had the vendo 44 running for a week.   It runs to cool to 36 Degrees, rest for 2-4 minutes then runs again.  I don't think there are any leaks that would cause it to warm, and it is well insulated.  Also the line freeze up as well as the coil.  The line freeze back to the condensor coils in the lower deck and back to the compressor.  Then it melts and runs water all over the kitchen floor. Too much freon or too little.   Is the thermostat located in the right place.  Should the inside fan run all the time?  
What do you think,    Dennis ,,  Memphis  '<img'>
Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5396


This is fine...everythings going to be OK....


WWW
« Reply #1 on: November 13, 2002, 09:43:17 am »

HI Droaten, I'm sure Eric will have more info for you than I can provide, but yes the inside evaporator fan does run all the time to circulate the cold air over the sodas, over Icing is probably an overcharge of Freon, or possibly too short of a capillary tube length (but if Eric helped you select the length it's probably OK) which might allow too much liquid back into the evaporator. short cycling can be caused by a defective T-stat, or one thats got an improper cut in point. the tip of the Themostat capillary tube  generally shouldn't be in the direct path of the evap's fan (cold air stream) try positioning it alongside of the evap coils so the cold air doesn't blow right at it, ( so it senses the returning airs temperature) hope it helps!  I'm sur Eric has more ideas than me.. post 'em so we all can learn ':<img:'>



Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
globalcompressors
Soda Jerks
*****
Offline Offline

Posts: 839


Global Compressors (Eric)


WWW
« Reply #2 on: November 13, 2002, 09:26:39 pm »

Thanks for the faith...I think. If I screw up, don't smoke me too bad! As Jonnie was saying, the the evaporator fan motor is supposed to run 24-7. A couple of other ideas. When you asked me for the proper cap tube size, did you tell them medium temp and what freon? I'm sure you did and that brings be to my next thought. Did you change the fan blade for the evaporator? If it is a different cfm, the air flow will be altered causing a freeze up of the coil and the return line to the compressor. Next, at 36 degrees the pressure should be around 12-15 psi on the low side. I noticed that the compressor cycles off for only 2-4 minutes. This is too often. Try putting a couple of gallons of water, in containers, inside the machine. This will help hold the temperature for longer periods of time between cycles. An empty machine will not hold temp as well as a machine full of product. This might give more time for the condensation to drain off the coils before freezing up again. Last, if the door seal is good, check the drain line. Make sure there is a "p" trap to prevent outside air getting into the box. That's about all I can help with without having the machine here in the shop. I really hope this helps out!!!! '<img'>

Eric ':cool:'
Logged

how's that OBAMA CARE workin' out for ya?
Guest
« Reply #3 on: November 14, 2002, 07:29:06 pm »

Thanks Johnnie G and Eric.   You are most helpful and responsive.  I will try all the suggestions.  

DRoaten  '<img'>
Logged
Pages: [1]   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!