Author Topic: Cavalier CDG-C Pressures w/134a?  (Read 4384 times)
0 Members and 1 Guest are viewing this topic.
rbbcdb
Guest
« on: August 02, 2010, 05:42:55 pm »

New compressor, cleaned throughout, new condenser motor and ready with 134a charge (supposedly)...what should the pressures be at 1)  Warm box start up, 90 degree ambient,  2)  Cooler operational for 2 hours, same temp?  The discharge line at evap is frosting up as well as shell.  Compressor never cycles.  I have no way of knowing the weight of the charge, but if I can pinpoint ambient and pressures/temps can I not confidently adjust charge?
Logged
loman4ec
Soda Jerks
*****
Offline Offline

Posts: 4768



« Reply #1 on: August 03, 2010, 11:37:44 am »

did you vacuum the system? you have two draw a vacuum before charging. you also need gauges to accurately know how much coolant to put in. Refrigeration is not something for a do it yourself project unless you have the proper knowledge and equipment. Its not as easy as it looks.
Logged
rbbcdb
Guest
« Reply #2 on: August 03, 2010, 12:08:14 pm »

System was evacuated multiple times, but the charge was not weighed in.  Scales were in the field.  I guess it sounds like I need to reclaim it and weigh it in.  Along those lines, what is the proper quantity?  Somewhere I saw postings of 8 to 9 oz?  Does that sound close?  Necessary equipment is not an issue, just capturing it before it leaves the office is the challenge. 
Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5396


This is fine...everythings going to be OK....


WWW
« Reply #3 on: August 06, 2010, 09:20:17 pm »

keep in mind that the capillary tube plays a key role in regulating the freon to the evaporator, you've changed the freon form R12 to 134a & your cap' tube may be starving the evaporator, you should change the filter/dryer while you're at it...
« Last Edit: August 06, 2010, 09:22:47 pm by johnieG » Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.