Title: dixie narco 348 compresser problem Post by: kenokarz on August 05, 2008, 07:35:37 pm i have the dixie narco 348, the problem im having is the compresser
i think, i jumper the themostat and the compresser runs for about 5min than shuts offf , coil start to cool and than that it unit shuts down , if i leave unit jumpered it starts again after a few mins and shut off right away, is the compresser junk ??? Title: Re: dixie narco 348 compresser problem Post by: MoonDawg on August 05, 2008, 07:43:51 pm Don't junk anything until you install a 3 in 1 relay.
Title: Re: dixie narco 348 compresser problem Post by: kenokarz on August 06, 2008, 10:06:50 pm with out sounding to dumb :laugh: what is a 3-1 relay and how do i install,
and where would i get one , and can i install with a left handed monkey wench :help: Title: Re: dixie narco 348 compresser problem Post by: Pat Pixley on August 06, 2008, 10:16:52 pm Here is what one is you can get it at Grainger
4E238 Hard Start Assist Kit Hard Start Assist Kit, Voltage Rating 115 Volts, Power Rating 1/4 thru 1/3 HP SUPCO RC0-410 http://www.grainger.com/Grainger/items/4E238 Title: Re: dixie narco 348 compresser problem Post by: Pat Pixley on August 06, 2008, 10:32:12 pm and this is from JohnieG
the spade (male) connector on the small relay that has the other two wires going to the compressor pin terminals, should have the "hot" wire that comes from the thermostat. the other end of the overload protector should be connected to line neutral. http://soda-machines.com/component/option,com_smf/Itemid,29/action,dlattach/topic,7133.0/attach,5780/image/ Title: Re: dixie narco 348 compresser problem Post by: kenokarz on August 06, 2008, 11:26:16 pm that should help, looks like i can install with out the left handed sky hook also :laugh:
thanks for the info i will order one tomorrow Title: Re: dixie narco 348 compresser problem Post by: kenokarz on August 20, 2008, 08:29:50 am update on the 3-1 relay, 1st i removed the unit from the machine, very easy 2min tops
wired in the relay and bench tested and the compressing unit bad :censored: any way, replaced the unit all is well, till next time , thanks to every one on this , now i know how to put in a 3-1 relay very easy for anyone to do, |