Title: Ideal 55 Post by: zadd on December 03, 2007, 08:17:09 pm On a ideal 55 if the lower lines frost almost back to the compressor , is this a sign of a over charger or under charge? :help:
Title: Re: Ideal 55 Post by: johnieG on December 03, 2007, 08:42:00 pm if the machines system hsn't been tampered with or serviced lately, it could a undercharge situation, are there any signs that the system was serviced ( tap-valves added, or a new filter-dryer added to the lines, etc.) or HAVE you had the system serviced latley? it may also be a restriction in the line(s).
so what happened when? Title: Re: Ideal 55 Post by: zadd on December 03, 2007, 09:23:54 pm I just had it recharged after pulling the lines and liner out . Recharged it to 9oz like the unit said. Some one has put a valve on it at one time.
Title: Re: Ideal 55 Post by: MoonDawg on December 03, 2007, 09:34:41 pm Ah yes, I had a system recharged one time and the frost
built up way too low on the line. So we let a little freon out and it performed fine from then on. Title: Re: Ideal 55 Post by: zadd on December 03, 2007, 10:40:11 pm I slowly let out some freon until I couldn't see the frost build up on the line anymore . I hope not to much :hopefull: It's cooling just fine ,problem solved so far. Thanks :smile:
|