Trouble-Shooting => Refrigeration => Topic started by: bubba on December 12, 2006, 01:51:46 pm



Title: Frost
Post by: bubba on December 12, 2006, 01:51:46 pm
The machine we have in the shop here is a DN7 selection bubble front. The evaporator is freezing up, including the t-stat probe... I defrosted it this morning, and the compressor came on and I thought all was good. I Just checked it again, and ice is building up again on the evap. Whats going on... the upper fan is running, and the condensor fan is running.. is it just low on freon? It has R134a in it....


Title: Frost
Post by: globalcompressors on December 12, 2006, 07:12:54 pm
Freezing in the corner/top only or the whole coil, top to bottom?


Eric


Title: Frost
Post by: bubba on December 12, 2006, 08:23:56 pm
Just freezing on the side where the loops are, and where there is a capilary tube coiled up, I assume (I know) its part of the thermostat. Its kinda hard to tell. I'll try to get a few pics before I try to defrost it tomorrow.


Title: Frost
Post by: collecture on December 12, 2006, 09:46:26 pm
Is the compressor cycling or running continuously? It might be the T-stat if it does not cycle.


Title: Frost
Post by: globalcompressors on December 12, 2006, 09:47:14 pm
No need,

The cap tube, right there where the coil is, is not the thermostat

probe. That is the cap tube itself. The thermostat probe, on a Dixie,

is located along the back edge if the upper shroud. If you are

freezing in that corner, you unit is low. If the unit has the

"snail coil" condenser coil, that's common. I'm not sure why but the

evaporator springs leaks. 80% of the Dixie units I repair are this

type. Add a little 134 and you'll be fine. When it gets worse, give a

hollar!

Eric


Title: Frost
Post by: cvb141 on December 12, 2006, 11:07:35 pm
I have a Dixie Narco that also was leaking on the evaporator end tubing just like Eric stated. Soldered it up, changed drier, pulled vacuum and charged it back up. I'm hoping it won't do it again else where.
Jerry


Title: Frost
Post by: bubba on December 13, 2006, 08:20:01 am
Tom... I believe the compressor is running constantly, but it is not getting cold.


Eric... I think you hit it on the head... its right in the upper corner and the whole suction line is frozen... The cap tube is coiled up and is not part of the t-stat, and it does have that stupid condenser coil.... Is there a repair needed to fix the leak, or is it a mystery leak? Since there are no service fittings, is it better to drain the system and weld in a fitting, or use one of the quick ports? I know those ports suck, but......


Title: Frost
Post by: globalcompressors on December 13, 2006, 01:33:35 pm
In this case, I wouldn't feel too bad using a "clamp" valve. The

evaporator coil usually leaks within the fins themselves. Very hard

to detect, very hard to repair. Sometimes, the leak can be in the

side tube loops and can be repaired. Either way, it requires a

torch and solder. Bump the charge, replace the unit when it gets

bad enough.


Eric


Title: Frost
Post by: bubba on December 13, 2006, 04:03:18 pm
Thanks Eric... I'll give it a whirl... :D


Title: Frost
Post by: globalcompressors on December 14, 2006, 08:15:46 pm