Trouble-Shooting => Refrigeration => Topic started by: pepsibob on October 03, 2016, 04:29:00 am



Title: hires ideal 55 freezing up
Post by: pepsibob on October 03, 2016, 04:29:00 am
I just pluged in my hires ideal 55 . line coming from compressor freezing up. what would cause this low Freon? thanks


Title: Re: hires ideal 55 freezing up
Post by: MoonDawg on October 03, 2016, 11:00:12 am
 Is the rest of the cooling compartment cold, and is the compressor cycling on an off?  If so it may be overfilled with freon.


Title: Re: hires ideal 55 freezing up
Post by: pepsibob on October 03, 2016, 01:08:53 pm
The in side is frosted also didn't listen for cycling


Title: Re: hires ideal 55 freezing up
Post by: MoonDawg on October 03, 2016, 04:42:27 pm
       Thermostat may not be working then!


Title: Re: hires ideal 55 freezing up
Post by: johnieG on October 04, 2016, 12:55:48 pm
1: bad thermostat not shutting off compressor

2: overcharge system (too much freon)

3: evaporator lines are broken loose from sides of liner, this would also cause a warmer that expected tank temperature ( IE; not cold enough inside) and a longer compressor run-time because themostat sees box as too warm & calls for compressor more often or runs it longer.

4: thermostats capillary sensing end isn't in good contact with tank wall, again causing long run times or never shutting off 

5: wrong thermostat for application