Not really so much as a question, as much as a clarification. About the thermal relay on the side of the compressor. I thought the whole point of that relay was if the compressor overheats, it shuts itself off, but when using a 3n1 you bypass that thermal relay, but how does the relay inside the 3in1 know if the compressor is overheating, if its not on top of the compressor?


Title: Re: Quick Question on a 3in1.
Post by: johnieG on July 13, 2011, 06:18:15 pm
The thermal overload on the side of the compressor, is really more of an over-current device, it will over-heat it's bi-metal disk when too-much current it passed & it will then "click" and disconnect power to the compressor until it cools down ( and then re-connect the power)

the 3-in-1 uses the same principle to protect the compressor, that's why it's important not to over-size the unit in regards to the compressor you're using it on ( IE: a 1/2 HP unit on a 1/4HP compressor)


Title: Re: Quick Question on a 3in1.
Post by: prestonrichmond on July 13, 2011, 07:43:52 pm
Thankyou very much  Johnie for the clarificationm