SMC Discussion Areas
May 06, 2024, 07:24:11 am *
Welcome, Guest. Please login or register.

Login with username, password and session length
News:
 
   Home   Help Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: Ambient temp for a cooling unit outside of a machine?  (Read 3338 times)
0 Members and 1 Guest are viewing this topic.
tkaz
Soda Jerks
*****
Offline Offline

Posts: 1900

tkaz


WWW
« on: March 31, 2011, 05:51:05 pm »

I just finished up my V-90 cooling system, and everything seems to be working great on it, compressor runs great after 2 years of sitting.  I don't have the machine to test it out in, but it is blowing cool air, which gets down to about 55 degress at the back of the evaporator unit.  Is that a normal temp for a unit sitting in the open air, is there some way I can test it all out without having it in the machine?
Logged

MoonDawg
Soda Jerks
*****
Offline Offline

Posts: 6224



« Reply #1 on: March 31, 2011, 06:01:49 pm »

       If you block the evaporator fan and let it run for a while, you will want to see all of the coils ice up. If for example.......8 out of 9 ice up, then it may be slightly low on freon.
Logged

Glen
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #2 on: March 31, 2011, 06:02:33 pm »

Temporarily put it in a big cardboard box that approximates the machines interior size, tape it up & with a remote reading thermometer monitor the temperature check the units cycling.
Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
tkaz
Soda Jerks
*****
Offline Offline

Posts: 1900

tkaz


WWW
« Reply #3 on: March 31, 2011, 07:09:12 pm »

Thanks johnieg, great solution.  Put the box around it and sealed it somewhat, got down to 27 degrees, compressor kicked off, and its cycling fine now.  Nice to know its still in good shape. 

Always great advice from you guys out here, appreciate it.
Logged

collecture
Soda Jerks
*****
Offline Offline

Posts: 6959


Tom


« Reply #4 on: March 31, 2011, 07:16:25 pm »

Maybe this topic should be a "Tips & Tutorial" section topic??
Great solution Johnie!
Logged

Cav 27, 33, CS-55E-2, 72
S-48 DP
Ideal CC 35, Barq's 55
1930s DP Counter Cooler
Vendo Coin Changers (ea. style - orig w/ stand)
Vendo Junior (rest.), 23 Deluxe, 39D, 44, 56RT, 80SS, 81A (orig), 81D, 6 C.V.
VMC 27, 27A, 81D DP, 110 DP
Westy WC-42-T, WC-44SK, WD-5(2), WB60
Victor C-14
Pages: [1]   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!