SMC Discussion Areas
May 19, 2024, 09:19:31 am *
Welcome, Guest. Please login or register.

Login with username, password and session length
News:
 
   Home   Help Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: dixie narco 348 compresser problem  (Read 4677 times)
0 Members and 1 Guest are viewing this topic.
kenokarz
Guest
« on: August 05, 2008, 07:35:37 pm »

i have the dixie narco 348, the problem im having is the compresser
i think, i jumper the themostat and the compresser runs for about 5min
than shuts offf , coil start to cool and than that it unit shuts down , if i leave unit jumpered it starts again after a few mins  and shut off right away, is the compresser junk Huh?
Logged
MoonDawg
Soda Jerks
*****
Offline Offline

Posts: 6224



« Reply #1 on: August 05, 2008, 07:43:51 pm »

     Don't junk anything until you install a 3 in 1 relay.
Logged

Glen
kenokarz
Guest
« Reply #2 on: August 06, 2008, 10:06:50 pm »

with out sounding to dumb  laugh what is a 3-1 relay and how do i install,
and where would i get one , and can i install with a left handed monkey wench help
Logged
Pat Pixley
Guest
« Reply #3 on: August 06, 2008, 10:16:52 pm »

Here is what one is  you can get it at Grainger

4E238
      Hard Start Assist Kit
Hard Start Assist Kit, Voltage Rating 115 Volts, Power Rating 1/4 thru 1/3 HP  SUPCO
RC0-410 

http://www.grainger.com/Grainger/items/4E238
« Last Edit: August 06, 2008, 10:22:57 pm by Pat Pixley » Logged
Pat Pixley
Guest
« Reply #4 on: August 06, 2008, 10:32:12 pm »

and this is from JohnieG

the spade (male) connector on the small relay that has the other two wires going to the compressor pin terminals, should have the "hot" wire that comes from the thermostat. the other end of the overload protector should be connected to line neutral.

http://soda-machines.com/component/option,com_smf/Itemid,29/action,dlattach/topic,7133.0/attach,5780/image/
« Last Edit: August 06, 2008, 10:36:16 pm by Pat Pixley » Logged
kenokarz
Guest
« Reply #5 on: August 06, 2008, 11:26:16 pm »

that should help, looks like i can install with out the left handed sky hook also  laugh
thanks for the info i will order one tomorrow
Logged
kenokarz
Guest
« Reply #6 on: August 20, 2008, 08:29:50 am »

update on the 3-1 relay, 1st i removed the unit from the machine, very easy 2min tops
wired in the relay and  bench tested and the compressing unit bad censored any way,
replaced the unit all is well,  till next time , thanks to every one on this , now i know how to put in a 3-1 relay very easy for anyone to do,
Logged
Pages: [1]   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!