SMC Discussion Areas
May 15, 2024, 02:46:03 pm *
Welcome, Guest. Please login or register.

Login with username, password and session length
News:
 
   Home   Help Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: to much or not enough freon?  (Read 2469 times)
0 Members and 1 Guest are viewing this topic.
Camel24hrs
Guest
« on: December 26, 2007, 06:30:32 pm »

Okay, I left the hoses hooked up to my cav7-486 over the holidays and what r-12 I had in it mostly leaked out.  I did not have anymore r-12 so I put in Freeze-12.  Running I have a suction pressure of 20 pounds and the box is cycling on and off at 35 degrees.  I have the thermostat set around 1, so I barely have it on.  Sounds good but, when the compressor runs I have frost build up on the suction line and on the side of the compressor.  Do I have enough Freon in it?  Or do I have to much?  Also it is about 40 degrees ambient temp, will that cause it to frost instead of sweat?

12-28-2007  Yep definately had it overcharged.  Problem solved.
« Last Edit: December 28, 2007, 11:45:28 pm by Camel24hrs » Logged
Pages: [1]   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!