SMC Discussion Areas
May 29, 2024, 02:38:50 pm *
Welcome, Guest. Please login or register.

Login with username, password and session length
News:
 
   Home   Help Login Register  
Pages: [1] 2  All   Go Down
  Print  
Author Topic: Uss-64 compressor will not turn off  (Read 8402 times)
0 Members and 1 Guest are viewing this topic.
SquareTopCollector
25 Cent Member
****
Offline Offline

Posts: 381



« on: February 05, 2012, 03:45:47 pm »

One of my cavilers compressors will not shut off. I swapped the T stat with another machine and it didn't solve the problem. What should I trouble shoot next? Can it be a relay? The compressor will turn off manually with the T stat dial.

Thanks
« Last Edit: February 05, 2012, 04:45:25 pm by SquareTopCollector » Logged
Yarochrehc
Soda Jerks
*****
Offline Offline

Posts: 787



« Reply #1 on: February 05, 2012, 07:14:02 pm »

Is the machine cooling OK?
 It sounds like you might have either a refrigerant problem or the evaporater fan is not working or something worse.
Logged

Bob

Restored
Vendo H63B  Coke in use in basement
Original
Vendo V/VF63/7  Pepsi in use

Restoring: Glascock Standard
(2) Vendo 63
(2)Vendo 90
Vendo 126  waiting for paint
VMC 56
Westinghouse WE-6
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #2 on: February 05, 2012, 07:15:42 pm »

it may be time for a new thermostat. they're wired just like a temperature controlled "light-switch"  it's either on or off, so if it's stuck "on" try to give it a playful "rap" on the nose ( the knob-shaft) with the handle end on a screwdriver, sometimes the contacts just weld themselves together & stick closed (On) ... oops
Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
SquareTopCollector
25 Cent Member
****
Offline Offline

Posts: 381



« Reply #3 on: February 05, 2012, 09:54:16 pm »

It gets really cold. The evap fan runs strong. The evap coils ice over. T stat is from a css-84 that works fine. I will knock it with a rubber mallet but I think it's something else. The line does have a tap on it.
« Last Edit: February 05, 2012, 10:10:36 pm by johnieG » Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #4 on: February 05, 2012, 10:05:58 pm »

don't use a mallet, use a screwdriver handle & a light "tap pity-tap" , or if you're determined to crush the poor thing, how's about a nice brick?  is the T-stat out of your CSS-84 the same type as the one you're trying to replace? and does the sensing end mount in the same spot? ( in the air vs mounted on the evap' coil housing ) or just replace the thermostat for Pete's sake. I'm out... glare
« Last Edit: February 05, 2012, 10:13:22 pm by johnieG » Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
SquareTopCollector
25 Cent Member
****
Offline Offline

Posts: 381



« Reply #5 on: February 05, 2012, 10:21:05 pm »

The CSS and USS are similar. T stats are mounted in the same place.   By the way I need a new fan for the CSS, where can I buy one?
Logged
briandr1
25 Cent Member
****
Offline Offline

Posts: 459



« Reply #6 on: February 05, 2012, 10:56:23 pm »

Johnstom supply or grainger will have replacement fan motors. If the comp is shutting off with the switch that tells you the problem is from the thermostat. I have one that the contacts stick sometimes and a tap wiyh a screw driver makes it open. Johnnie is right replace t stat. good luck
Logged

selectivend 64 sa
2 cavalier 96
1975 bally hi deal em pinball machine
1920 wate and fate penny  scale
SquareTopCollector
25 Cent Member
****
Offline Offline

Posts: 381



« Reply #7 on: February 05, 2012, 11:09:20 pm »

I don't need the motor just the blades. One cracked
Logged
briandr1
25 Cent Member
****
Offline Offline

Posts: 459



« Reply #8 on: February 05, 2012, 11:19:01 pm »

i have a set of blades from a cavalier round eveporator would prob work for you
Logged

selectivend 64 sa
2 cavalier 96
1975 bally hi deal em pinball machine
1920 wate and fate penny  scale
MoonDawg
Soda Jerks
*****
Offline Offline

Posts: 6224



« Reply #9 on: February 05, 2012, 11:22:00 pm »

       If you have already switched the thermostat with a similar "known working" unit and it acts the same, I'm not sure a brand new one will work any better. If they both manually switch off the compressor, the wiring must be ok too.
      I would suggest moving the capillary tube to different locations on the evaporator, as it seems there may be a cold sensing problem.
     
Logged

Glen
Pages: [1] 2  All   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!