SMC Discussion Areas
May 15, 2024, 01:49:48 pm *
Welcome, Guest. Please login or register.

Login with username, password and session length
News:
 
   Home   Help Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: Icing up  (Read 4359 times)
0 Members and 1 Guest are viewing this topic.
Guest
« on: August 09, 2005, 08:13:45 am »

I started my machine (USS-96) last night and then checked it this morning.  I cools very very good, but I have ice on the lines in the bottom.  It was on the lowest setting and I think that I may need a new thermostat.

Can anyone confirm this and tell me how to change one and what to look for when I buy one?  Would home depot have them?   '<img'>
Logged
BryanH
Soda Jerks
*****
Offline Offline

Posts: 1356


Sweatin' in Arizona... but it's a dry heat!


WWW
« Reply #1 on: August 09, 2005, 11:19:04 am »

Jed - any refrigeration supply company should have the t-stats.  Icing might also be caused by a bad door seal that lets air (and moisture) into the cooling area.
Logged

Thanks, Bryan
   Cavalier USS-96: unrestored, working on the back patio
   CV VUB/C 8-91: a fantasy restoration?
   GE Cooler: in pieces, my next project
Guest
« Reply #2 on: August 09, 2005, 12:15:12 pm »

The icing is on the lines in the lower compartment on the lines coming out of the compressor.  Sorry I wasn't more clear.  ':blushing:'  

I'm not sure if it is shutting off at all? '<img'>




Logged
Kevin C
Soda Jerks
*****
Offline Offline

Posts: 971



« Reply #3 on: August 09, 2005, 02:07:40 pm »

Hello

Take the old T-stat off & take it to your local AC supply store. They will have what you need. It should an easy change out by disconnecting the two electrical lines on the back of the t-stat.

Kevin
Logged

Vendo 63-C   On the job
Vendo 56   Going back together
Vendo 56-C    Waiting for rehab!
Vendo 126  Rough outside but loaded & operational
Vendo 110  Under repair
Ideal 55 -  **For Sale make offer
Glasco 55 -  Waiting
Royal 650  On the job
Lance Snack Machine - On the job
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #4 on: August 09, 2005, 02:27:12 pm »

icing of the line back towards the compressor (I'm assuming the capillary tube)  can also indicate an undercharged system, or possibly a restriction in the tubing due to an ice crystal in the line, kinking/crushing of the 'cap. tube, or some little fleck of crud restricting the capillary tube above the point were it normally would join the suction line at the evaporator... '<img'> , you might wish to talk to Eric over at Global compressors & tell him the symptoms...just a thought.



Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
Guest
« Reply #5 on: August 09, 2005, 02:48:28 pm »

Sounds like I may have more of a problem than I thought.  I will give Eric a call and go home tonight and check for any kinks in the hose.
Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #6 on: August 09, 2005, 06:45:52 pm »

"Tubing"  Hoses are for lawn sprinklers!  '<img'>  ( had to harass you!) yes please give Eric a call.
Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
Guest
« Reply #7 on: August 09, 2005, 07:39:04 pm »

Doh.... ':blushing:'

The good news is there are no kinks in my...tubing.  ':<img:'>




Logged
Pages: [1]   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!