Trouble-Shooting => Refrigeration => Topic started by: Jake777 on September 27, 2016, 11:23:59 am



Title: Do I still need a run capacitor?
Post by: Jake777 on September 27, 2016, 11:23:59 am
Not very experienced at all when it comes to wiring this is my first project when it comes to this stuff. I am re-wiring my westinghouse wd10 and I have two new fan motors that are single phase. Does this mean I no longer need the run capacitor? I've attached my wiring diagram below. So If I no longer need it I would just connect the fan motor wires to the number 2 & 3 terminals as opposed to numbers 4 & 5 as it was originally, correct? And then for the condenser fan motor the two wires would connect to the run winding and common terminals on the compressor?



Title: Re: Do I still need a run capacitor?
Post by: johnieG on September 30, 2016, 05:28:23 pm
Yep, you don't need the phase-split / run capacitor with the new single phase replacement motors, The Evap' fan-motor will wire across terminal no.s 2 & 5, & the Condenser fan-motor will wire across terminals "W" & "B"


Title: Re: Do I still need a run capacitor?
Post by: Creighton on September 30, 2016, 06:28:50 pm
Great info !!
Creighton


Title: Re: Do I still need a run capacitor?
Post by: Jake777 on October 02, 2016, 07:51:31 pm
All figured out.