Author Topic: Jacobs refridgeration  (Read 11749 times)
0 Members and 1 Guest are viewing this topic.
r500
Newbie
*
Offline Offline

Posts: 27


« Reply #10 on: December 16, 2009, 09:13:17 pm »

  Sounds like the contact point in the thermostat is welded shut. Replace the t-stat.  Have your a/c guy come back and and check that the charge is right,  have him raise the head pressure to 30 deg. above ambent temperature and monitor box temp. when it reaches set point make sure head presure is at 30deg. above ambent temperture and the charge should ok.  These boxes have a cap tube and are critically charged systems.
« Last Edit: December 16, 2009, 09:15:16 pm by r500 » Logged
davethebirdman
Soda Jerks
*****
Offline Offline

Posts: 3162



« Reply #11 on: December 19, 2009, 11:33:20 am »


Thanks for your advice... The T Stat I ordered from Funtroincs arrived today... I have fitted it and its still got the same fault..

Its running and getting cold but If I turn the T Stat off the compressor just contiunes to run...

I'm at a bit of a loss....

Th is old girl is almost four years into her restoration and I thought I had it solved with the new T Stat...

Dave
Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #12 on: December 19, 2009, 12:43:27 pm »

Again, sounds like your compressors getting some back-feed voltage from somewhere,

so say if you'd open/disconnect the wires & insulate them (temporarily with electrical tape)from the back of the thermostat. I assume the compressor will still be running?

I know some older machines have a large start/run relay assembly that's housed in a large tin box, and the start/run relay in this type of setup is controlled by the thermostat, but the compressor doesn't get any direct line voltage delivered to it from the thermostat itself, 

if this is the case you may have a pair of spot-welded contact points in the start-run relay itself which wouldn't allow it to shut off no matter what the thermostats set at.

Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
davethebirdman
Soda Jerks
*****
Offline Offline

Posts: 3162



« Reply #13 on: December 19, 2009, 12:52:23 pm »


Hi Johnie...

The compressor doews have a large tin box with the start-run realy in it you're right...

I haven't actually put the two wires together to see if it will just continue to run but I'm gueesing that it will..

Its night time here now.. Will try the two wires togther tomorrow...

Is it possible to by pass the compressor start- run with a 3 in 1...?

Dave
Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #14 on: December 19, 2009, 01:14:46 pm »

Dave...I meant that you should remove the wires from the thermostats' terminals & tape them up (so they don't short out or shock you) & see if the compressor still runs continuously, 

Yes it's possible to use a 3-in-1 in place of the original start/run relay, does your compressor have three external binding posts/terminals ( three in a row, as opposed to a modern compressors three in a triangular pattern)?   
Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.
davethebirdman
Soda Jerks
*****
Offline Offline

Posts: 3162



« Reply #15 on: December 19, 2009, 02:15:25 pm »



Hi Johnie

this is a picture of the terminal block on the compressor...

What do you reckon??

Dave
Logged
johnieG
Global Moderator
Soda Jerks
*****
Offline Offline

Posts: 5387


This is fine...everythings going to be OK....


WWW
« Reply #16 on: December 19, 2009, 03:17:11 pm »

Is the wiring as shown original?

OK, Good...the terminal with the copper strap is definitely the "common" connection, ( sometimes marked/stamped on the metal case as "C" for "common")

the Red wire should be "Run" ( sometimes marked/stamped on the metal case as "M" for "main")

the white wire should be "start"  ( sometimes marked/stamped on the metal case as "S" for "start")

The better way to check is to remove all the wires from the terminals, & use an OHM meter to measure the Resistance readings between the COMMON terminal & the other two, the HIGHER reading is the start terminal, the LOWER reading is the run terminal.
Logged

Spoon-feeding Newbies since 2001...Wink
Yeah..220,221 whatever it takes.
Remember, all it needs is a shot of Freon!
The Vendo V-83 is the '59 Edsel of the coke machine world. ;p
Spray painting does NOT restore a compressor
11 is louder than 10...
"Hope" is good, but it's not an action plan.