jimstl99:
Here is one I can't seem to figure out....
I picked up a Cavalier C-55D recently and have been sprucing it up a bit. Finally plugged it in and it vends properly (with coins) and lights work. Hurrah! However, I don't ever hear the compressor kick on. I thought I would check the thermostat to see if it was turned off but I can't find it. Where is it hidden? I'm baffled.
Thanks in advance,
Jim
Jim:
Can you locate any electric wires headed toward the evaporator...? One would be for the fan, the other would be a thermostat. There will be other wire(s) for the vending mech as well.
jimstl99:
I guess I just can't find it or it isn't there. I have a decent view of the evaporator and can't trace anything to a thermostat. Hopefully someone who has this model will let me know where theirs is mounted.
Thanks.
jim
johnieG:
some machines ( like Westinghouse's) had the thermostats control & dial mounted remotely down by the compressor area & only the sensing unit ( sometimes called the"bulb") in the evaporator area or clamped directly to the evaporator or located ina thermostat "well" ( a hollow length of copper tube) to protect the sensing end of the capillary.
collecture:
I have the two-selection C55 and you have to remove the left back spacer to access it at the bottom. Not sure if the single selection is different, but doubt it.