Rookie leak question
Pages: [
1
]
Go Down
« previous
next »
Print
Author
Topic: Rookie leak question (Read 395 times)
0 Members and 1 Guest are viewing this topic.
Guest
Rookie leak question
«
on:
July 09, 2006, 01:44:36 pm »
I have a Choice-Vend CVC-168 circa early 1970's...
R-12. I have used Johnsen's Freeze-12 in the past (2+ years ago to boost it. It runs fine, except when it's turned off. Anytime it's allowed to be unplugged for a day or more, it no longer cools effectively when turned back on. I have to add a little Freeze-12 everytime. Sounds like a leak; but why wouldn't it leak while it was running, too?
I don't know squat about refrigeration units, other than adding the Freeze-12 every few years.
I know I'm living on borrowed time with this unit and will eventually have to get it replaced, but I'd like to know what causes this and why it works as long as it's running?
Thanks - Mark
Logged
davethebirdman
Soda Jerks
Offline
Posts: 1585
Rookie leak question
«
Reply #1 on:
July 09, 2006, 02:37:48 pm »
Nice Seeburg....
Logged
One V-39 the good old faithful
Jacobs 50 - Feeling sorry for itself in the garage
V-56 - back from the dead
Wurly 1900 - Blasting away
Rockola Empress - Gleaming like new
Seeburg JL - A bit tempremental (Like its owner)
Couple of Candy wall hangers
Couple of Seeburg Wallboxes
Guest
Rookie leak question
«
Reply #2 on:
July 09, 2006, 02:53:36 pm »
Quote
(davethebirdman @ July 09 2006,2:37)
Nice Seeburg....
Thanks Dave. I finished it last year. Man, had I known what the re-chroming was gonna cost, I would have bagged it! But, I really like it. I have 1 wall box hooked up to it. It seems to select one record off of the one it's supposed to (just the wall box selector - the main one works fine).
Let's see yours!
Logged
davethebirdman
Soda Jerks
Offline
Posts: 1585
Rookie leak question
«
Reply #3 on:
July 09, 2006, 03:00:25 pm »
Re-Chroming ain't cheap but well worth it in the long run.
I had a similar problem with one of my wallboxes I just moved the selection strips on one. Nobody ever knew the problem exisited. It get complicated when you want to change a record though.
Good luck with you techie question someone here will answer it for you shortly I'm sure. I currently have two compressors sitting in my garage. Neither of them have been powered up for at least 20 yrs. Keeping my fingers crossed that when I get round to it they'll fire up okay. Otherwise its going to be expensive.
Dave
Logged
One V-39 the good old faithful
Jacobs 50 - Feeling sorry for itself in the garage
V-56 - back from the dead
Wurly 1900 - Blasting away
Rockola Empress - Gleaming like new
Seeburg JL - A bit tempremental (Like its owner)
Couple of Candy wall hangers
Couple of Seeburg Wallboxes
johnieG
Global Moderator
Soda Jerks
Offline
Posts: 2449
Rookie leak question
«
Reply #4 on:
July 09, 2006, 05:31:18 pm »
From what you've described, it sounds like a leak on the low (suction) side of the system, I'm assuming here, not being able to see the machine & set up my gauges on it, but here goes, when the system is off, the line pressure on the low & high side starts to equalize, from a low pressure of about 18psi
to around 60-70psi when every thing balances off, it could be a pinhole leak in your evaporator, when exposed to the higher line pressure leaks, but when you "top it off" & start it up, well know the lowside will below the pressure point that supports the leak, I'm not familiar with freeze-12's pressures in a system. you'd really need to put a set of gauges on the system to observe whats happening.
Logged
Yea, 220...221, whatever it takes.
globalcompressors
25 Cent Member
Offline
Posts: 393
Global Compressors (Eric)
Rookie leak question
«
Reply #5 on:
July 10, 2006, 07:35:34 pm »
Johnie,
You explained it perfectly...even more so if the machine is out in the garage
or on a back porch. Higher temperatures...higher pressures.
Eric
Logged
Cooling the World, one machine at a time...really!
Pages: [
1
]
Go Up
Print
« previous
next »
Jump to:
Please select a destination:
-----------------------------
The Coin Return
-----------------------------
=> Soda-Machines.Com News
=> Other Coin-Op's
=> General Chit Chat
=> Estimated Values
=> Tutorials & Tips
-----------------------------
Soda Machines, Coolers & Dispensers
-----------------------------
=> Pre 60's Machines & Coolers
=> Post 60's Machines & Coolers
=> Picnic Coolers
=> Syrup Dispensers
-----------------------------
Trouble-Shooting
-----------------------------
=> Coin Mechanisms
=> Refrigeration
=> Vending Mechanisms
-----------------------------
Restorations
-----------------------------
=> General
=> Refinishing
-----------------------------
The Vending Rack
-----------------------------
=> Swap Meet Area
Loading...