Author
Topic: Cycling (Read 314 times)
0 Members and 1 Guest are viewing this topic.
Guest
Cycling
«
on:
April 10, 2005, 11:06:33 pm »
I got my Vendo 90 running, it died, found out it was the thermostat. I changed thermostats and it works like a dream. However it seems to cycle about every ten minutes. Compare to my refridgerator it seems like it is way too often. Any ideas on what is "normal" and how to correct it?
Justin
Logged
loman4ec
Soda Jerks
Offline
Posts: 3005
Cycling
«
Reply #1 on:
April 10, 2005, 11:18:30 pm »
Is the machine full of soda? I know that soda is a great insulator and will make the machine more efficient. Also is there any leaks in the machine. Like a door seal. If so that would be the problem.
Logged
Guest
Cycling
«
Reply #2 on:
April 11, 2005, 01:13:33 pm »
No sodas in it yet, I have doing some test runs before. I can't notice any air leakage around the seals. Justin
Logged
johnieG
Global Moderator
Soda Jerks
Offline
Posts: 2449
Cycling
«
Reply #3 on:
April 11, 2005, 08:42:49 pm »
Quote
(JustinBoots @ April 10 2005,11:06)
I got my Vendo 90 running, it died, found out it was the thermostat. I changed thermostats and it works like a dream. However it seems to cycle about every ten minutes. Compare to my refridgerator it seems like it is way too often. Any ideas on what is "normal" and how to correct it?
Justin
Where did you get the Theromstat? & did it come with a Spec. sheet (specification & information guide) that specifies the cut-in & cut-out & temperature range of the thermostat?
Logged
Yea, 220...221, whatever it takes.
Guest
Cycling
«
Reply #4 on:
April 11, 2005, 08:46:58 pm »
put on a Robertshaw 3040 cold control unit from my local refridgeration supply house. The only specs on it are FL = 20 amps LR = 96 amps. Justin
Logged
globalcompressors
25 Cent Member
Offline
Posts: 393
Global Compressors (Eric)
Cycling
«
Reply #5 on:
April 16, 2005, 09:12:59 am »
Justin,
You need to know if the thermostat is a "contact" style or an "air probe" style. If it is an air sensor style and is making contact with the evaporator coil tubing, it will read the coil temperature and not the box temperature resulting in compressor "short cycle". Try moving the probe placement around and see if that helps.
The other thing is to have a full box as Loman had suggested. If the box is full of product, it will hold temperature for longer periods between compressor cycles.
Eric
Logged
Cooling the World, one machine at a time...really!
Pages: [
1
]
Go Up
Print
« previous
next »
Jump to:
Please select a destination:
-----------------------------
The Coin Return
-----------------------------
=> Soda-Machines.Com News
=> Other Coin-Op's
=> General Chit Chat
=> Estimated Values
=> Tutorials & Tips
-----------------------------
Soda Machines, Coolers & Dispensers
-----------------------------
=> Pre 60's Machines & Coolers
=> Post 60's Machines & Coolers
=> Picnic Coolers
=> Syrup Dispensers
-----------------------------
Trouble-Shooting
-----------------------------
=> Coin Mechanisms
=> Refrigeration
=> Vending Mechanisms
-----------------------------
Restorations
-----------------------------
=> General
=> Refinishing
-----------------------------
The Vending Rack
-----------------------------
=> Swap Meet Area
Loading...